(→Performing the test) |
| Line 72: | Line 72: | ||
Using the cylinder measure out 50ml of IPA and pour it into the conical flask. The first thing we must do is blank the alcohol. Given that the IPA is likely to be acidic rather than alkaline, and that you will be using HCl to titrate, the easiest way would be to add some NaOH solution, used in titrating WVO, to the IPA. Then add a few drops of bromophenol blue indicator and then add your HCl solution until the solution just turns yellow. | Using the cylinder measure out 50ml of IPA and pour it into the conical flask. The first thing we must do is blank the alcohol. Given that the IPA is likely to be acidic rather than alkaline, and that you will be using HCl to titrate, the easiest way would be to add some NaOH solution, used in titrating WVO, to the IPA. Then add a few drops of bromophenol blue indicator and then add your HCl solution until the solution just turns yellow. | ||
| − | + | With the 10ml pipette draw up exactly 10ml of biodiesel and add it to the blanked IPA in the conical flask. Adding the Bio, which if it contains soap should be alkaline, should revert the colour again so that you can titrate it with the HCl solution. Turn on the magnetic stirrer and add more Bromophenol Blue indicator if required. The solution should now be a green/blue colour. Using the 0.2ml pipette, slowly, (drop wise) add the HCl solution until you reach the yellow end point. (You should be aware that the colour change can be very rapid if the soap content is low and care should be taken when adding the acid so that you do not exceed the point at which the yellow colour is achieved). Note how much HCl has been used and calculate for soap in ppm using the formula below. | |
Revision as of 22:00, 22 June 2011
- the 50/50 shake test
50/50 shake test
- 50/50 water shake up test
Assessing water clarity
- Shine a laser through it
- Water clarity tests
Titrated soap test
Required equipment
- magnetic stirrer.
- 100ml conical flask
- 50ml measuring cylinder
- 10ml pipette
- 0.2ml pipette
- Soap titration equipment
Performing the test
For NaOH derived biodiesel:
HCl used × 304 = ppm of soap
Understanding the results
