Ok, here are my findings.
All taken on the Potter & Brumfield 40A SSR which controls the processor heater on my plant
3KW heater connected to SSR and control input on :-
Supply terminal to neutral 233.1V
Load terminal to neutral 228.9V
3KW heater connected to SSR and control input off:
Supply terminal to neutral 234.2V
Load terminal to neutral 0.2v
Heater now disconnected from load terminal of SSR - control input on
Supply terminal to neutral 234.2V
Load terminal to neutral 234.2V
Heater now disconnected from load terminals of SSR - control input off
Supply terminal to neutral 234.2V
Load terminal to neutral 234.0V
Clearly this shows that, with no load, the Load terminal will be at full supply voltage IF no load is connected to it no matter what the control input is doing
But, with a load connected, it behaves as expected.
Effectively it controls the current flow but does not isolate the circuit from mains voltage.
This is a good reason to make sure that the supply is isolated before playing with anything downstream of an SSR. I suspect that the current flow through it, even when off would be enough to give a nasty shock.
This article from Omron states that the minimum load current for AC output SSRs is 100mA to ensure reliable switching which equates to around 24Watts at mains voltage.
https://www.ia.omron.com/support/faq/answer/18/faq02152/index.htmlThis one is a pretty good read too if you want to know lots about SSRs. It would appear that the snubber circuit (inside the SSR) is the cause of the supply voltage at the load terminal with no load.
http://docs-europe.electrocomponents.com/webdocs/0d82/0900766b80d82ad3.pdf